Any HVAC guys? Heat pump ?? #3206903
01/21/24 04:16 PM
01/21/24 04:16 PM
Joined: Jan 2003
Posts: 15,355
Omaha Ne
T
TJP Offline OP
I Live Here
TJP  Offline OP
I Live Here
T

Joined: Jan 2003
Posts: 15,355
Omaha Ne
I have a Carrier infinity system that is ~ 8 years old and has been fine until this year. it has been cleaned regularly. We have been through a BRUTAL cold snap the last 3-4 weeks. I will say we have gotten his cold previously but not for this length of time that I recall. To cut to the chase My concern / question is the amount of ice build up in the bottom pan I can't say for sure how thick it is but I would guess 1/4 to 1". It is below the coils. I am not sure if this is normal and if not how does one deice the pan? A bit more information follows.

The first problem noted was a pulsating noise when going into defrost. loud enough to be heard in the house.
The installer sent a service guy out. he checked the pressures and all seemed well. It went into defrost and the noise appeared.
He noted if he placed pressure on a front corner he could clearly feel the pulsing.
The unit had a fair amount of ice under and inside it with some frozen on the ground.
Raising the noisy corner seemed to help it a lot. It only made the noise one time after that and raising the same corner eliminated it again. I believe the unit may have been frozen the the stands and pan which was transmitting the noise.
A week or so went by and the unit threw a code 83 low pressure lock out. it was -10 or so.
Once it got back into the 20's I pulled the side panels and verified all was clean. The outermost drip holes were partially blocked so they were cleaned. There was a small amount of ice an some surface of the lower coils, not a lot or very thick, maybe an inch or so high in some areas. Again fairly small areas overall
using warm water and alcohol was able to get the lowest portion of the pan below the coils completely de iced and open.

The unit ran for about 2 hours and threw the code again. Temps have been as high as 25 with no change. We are running on backup electric heat and the installer is BURIED due to the unusual temps.

thanks for any input assistance beer

Re: Any HVAC guys? Heat pump ?? [Re: TJP] #3206977
01/21/24 07:57 PM
01/21/24 07:57 PM
Joined: Jul 2006
Posts: 1,295
New Jersey
P
Powerflow Offline
pro stock
Powerflow  Offline
pro stock
P

Joined: Jul 2006
Posts: 1,295
New Jersey
WAG: Partially stuck reversing valve. Try unplugging it to see if that helps. Be careful when working around electricity especially on wet ground.

Re: Any HVAC guys? Heat pump ?? [Re: Powerflow] #3207038
01/21/24 11:23 PM
01/21/24 11:23 PM
Joined: Jan 2003
Posts: 15,355
Omaha Ne
T
TJP Offline OP
I Live Here
TJP  Offline OP
I Live Here
T

Joined: Jan 2003
Posts: 15,355
Omaha Ne
Originally Posted by Powerflow
WAG: Partially stuck reversing valve. Try unplugging it to see if that helps. Be careful when working around electricity especially on wet ground.


thanks for the reply. Supposed to be getting into mid to high 30's this week, So I hope to get the ice out of the pan. Resetting it as suggested will likely work but I'd prefer to isolate and fix the issue before the next artic blast which may not be until next year. the unit has never done this before so i suspect something is amiss frown
Thanks again for responding wink
What does WAG: mean confused

Re: Any HVAC guys? Heat pump ?? [Re: Powerflow] #3207055
01/22/24 12:28 AM
01/22/24 12:28 AM
Joined: Jan 2003
Posts: 4,720
Moved to N.E. Tennessee
GomangoCuda Offline
master
GomangoCuda  Offline
master

Joined: Jan 2003
Posts: 4,720
Moved to N.E. Tennessee
Originally Posted by Powerflow
WAG: Partially stuck reversing valve. Try unplugging it to see if that helps. Be careful when working around electricity especially on wet ground.

Also be aware that there is a good size capacitor in there that can kill you even when the power is disconnected from the unit.

WAG = "Wild A$$ed Guess"

Last edited by GomangoCuda; 01/22/24 12:31 AM.

In theory, there is no difference between theory and practice. In practice, there is.
Re: Any HVAC guys? Heat pump ?? [Re: TJP] #3207084
01/22/24 08:18 AM
01/22/24 08:18 AM
Joined: Jan 2006
Posts: 8,162
USA
3
360view Offline
Moparts resident spammer
360view  Offline
Moparts resident spammer
3

Joined: Jan 2006
Posts: 8,162
USA
Using your Carrier model number search the internet, eBay and Amazon for a copy of the specific service manual.

At a certain outside temperature the efficiency of an air heat pump is so low that your hourly electric bill is equal to just using resistance heaters.

I would guess even for your 8 year old higher efficiency air heat pump
the “break even” outside air temperature is 25 degrees F plus/minus 4 degrees.

Re: Any HVAC guys? Heat pump ?? [Re: 360view] #3207336
01/22/24 10:08 PM
01/22/24 10:08 PM
Joined: Jan 2003
Posts: 15,355
Omaha Ne
T
TJP Offline OP
I Live Here
TJP  Offline OP
I Live Here
T

Joined: Jan 2003
Posts: 15,355
Omaha Ne
Thanks for the responses, I reset the unit today ( power on /power off). Code went away but then several things transpired that are totally whacky like the display saying the heat pumps running when it's not. HP and electric heat running when raising the t/sat by 1 degree, HP pump occasionally would run but slowly, then the Code popped up again. So have to wait until they come out. At least we have the electric back up wink beer
Note the outside temp realcrazy

DSC04639.JPG
Re: Any HVAC guys? Heat pump ?? [Re: TJP] #3207503
01/23/24 01:16 PM
01/23/24 01:16 PM
Joined: Feb 2014
Posts: 1,706
central il.
S
second 70 Offline
top fuel
second 70  Offline
top fuel
S

Joined: Feb 2014
Posts: 1,706
central il.
I needed a system reset on my Mitsubishi top of the line multi zone and they said the temperature had to be above 50 for the reset to work. What a bunch of s---h. Buy a unit that says it'll work to -15 which it does and produces heat @ 115 degrees but can't run long enough to produce enough heat without having to defrost. I've had it several years and to be honest once it's zero it's pretty much worthless. Mike

Re: Any HVAC guys? Heat pump ?? [Re: second 70] #3207668
01/23/24 10:35 PM
01/23/24 10:35 PM
Joined: Jan 2003
Posts: 15,355
Omaha Ne
T
TJP Offline OP
I Live Here
TJP  Offline OP
I Live Here
T

Joined: Jan 2003
Posts: 15,355
Omaha Ne
Originally Posted by second 70
I needed a system reset on my Mitsubishi top of the line multi zone and they said the temperature had to be above 50 for the reset to work. What a bunch of s---h. Buy a unit that says it'll work to -15 which it does and produces heat @ 115 degrees but can't run long enough to produce enough heat without having to defrost. I've had it several years and to be honest once it's zero it's pretty much worthless. Mike


this units been fine for 8 years, only locked out once at -28. This time it's a whacking out. Service tech scheduled for Thursday afternoon beer

Re: Any HVAC guys? Heat pump ?? [Re: second 70] #3207670
01/23/24 10:45 PM
01/23/24 10:45 PM
Joined: Jan 2003
Posts: 4,270
Morrow, OH
markz528 Offline
master
markz528  Offline
master

Joined: Jan 2003
Posts: 4,270
Morrow, OH
My new heat pump cooled fine in the summer but would not run on heat. At first it would trip on high pressure, then it would constantly trip on low pressure. Put the gauges on it and pressures were good in cooling but would drop to almost zero in heat mode.

Ended up being a bad heating side expansion valve. Mine is adjustable, and by fully exercising the adjustment screw, got it to work for about 30 minutes then same thing. Had to change it. My stupid 4 ton heat pump (top of the line 2 stage crap) takes 20 lbs of R410A!


67 Coronet 500 9.610 @ 139.20 mph
67 Coronet 500 (street car) 14.82 @ 94 mph
69 GTX (clone) - build in progress......
Re: Any HVAC guys? Heat pump ?? [Re: TJP] #3207783
01/24/24 12:57 PM
01/24/24 12:57 PM
Joined: Feb 2014
Posts: 1,706
central il.
S
second 70 Offline
top fuel
second 70  Offline
top fuel
S

Joined: Feb 2014
Posts: 1,706
central il.
Yeah I see on your picture that your unit switches to electric heat once it gets too cold. Almost all whole house units have that feature. Most people don't even notice. The only way to know it happened is when you look at the readout and the red electric heat light is on. The heat pump shuts off at a certain temp and runs 100% as an electric heater. My split mini doesn't have that feature. Good luck Mike

Re: Any HVAC guys? Heat pump ?? [Re: second 70] #3207947
01/24/24 10:59 PM
01/24/24 10:59 PM
Joined: Jan 2003
Posts: 15,355
Omaha Ne
T
TJP Offline OP
I Live Here
TJP  Offline OP
I Live Here
T

Joined: Jan 2003
Posts: 15,355
Omaha Ne
Originally Posted by second 70
Yeah I see on your picture that your unit switches to electric heat once it gets too cold. Almost all whole house units have that feature. Most people don't even notice. The only way to know it happened is when you look at the readout and the red electric heat light is on. The heat pump shuts off at a certain temp and runs 100% as an electric heater. My split mini doesn't have that feature. Good luck Mike

thanks,
Tomorrow is D-day and i will be really interested to see what they come up with. I will not be surprised if there is more than 1 issue asthis fiasco started several weeeks back and has displayed a myriad of symptoms the most common and consistent being the same fault code I'll keep you guys updated.
Thanks to all again
beer

Re: Any HVAC guys? Heat pump ?? [Re: TJP] #3208187
01/25/24 10:15 PM
01/25/24 10:15 PM
Joined: Jan 2003
Posts: 15,355
Omaha Ne
T
TJP Offline OP
I Live Here
TJP  Offline OP
I Live Here
T

Joined: Jan 2003
Posts: 15,355
Omaha Ne
Tech was out today, System was completely empty eek The muffler off the compressor had cracked well above the solder joint which he said was quite strange. So might be next week before he can get the replacement installed down beer

Re: Any HVAC guys? Heat pump ?? [Re: TJP] #3208284
01/26/24 01:12 PM
01/26/24 01:12 PM
Joined: Feb 2014
Posts: 1,706
central il.
S
second 70 Offline
top fuel
second 70  Offline
top fuel
S

Joined: Feb 2014
Posts: 1,706
central il.
Wow that's quite a surprise. Gee without the backup electric you would have been 100% without heat.

Re: Any HVAC guys? Heat pump ?? [Re: TJP] #3208326
01/26/24 04:43 PM
01/26/24 04:43 PM
Joined: Jan 2006
Posts: 8,162
USA
3
360view Offline
Moparts resident spammer
360view  Offline
Moparts resident spammer
3

Joined: Jan 2006
Posts: 8,162
USA
In your first post you mentioned noise and vibration, plus pushing down on a corner changing them.

That vibration should be a suspect in the root cause of the muffler crack.

Re: Any HVAC guys? Heat pump ?? [Re: 360view] #3209138
01/30/24 05:59 AM
01/30/24 05:59 AM
Joined: Jan 2006
Posts: 8,162
USA
3
360view Offline
Moparts resident spammer
360view  Offline
Moparts resident spammer
3

Joined: Jan 2006
Posts: 8,162
USA
Tuesday Wall Stree Journal on page A3 has article
“Heat Pumps Get Trial Runs in Bitter Cold”.

sample quote

Standard Heat Pumps operate efficiently at Outdoor temperatures down to 35 degrees F,
but newer cold weather systems can operate down to 7 degrees
- and engineers are pushing heat pumps to go further.”

end quote

Long article then goes on to explain that these more expensive new heat pump systems have frequency changing inverter driven variable speed AND double stage compressors.

These newest air exchange heat pump systems cost in the $7500 range
but the US Federal government currently has a $2000 tax rebate for the most efficient systems.

Ground coupled air pumps cost about $11,000 more.

Rheem is mentioned as a manufacturer aggressively competing to be the “winner” of annual DOE testing,
but the picture in the article shows a Mitsubishi.

Re: Any HVAC guys? Heat pump ?? [Re: 360view] #3209198
01/30/24 12:15 PM
01/30/24 12:15 PM
Joined: Oct 2007
Posts: 3,884
Oregon
hooziewhatsit Offline
master
hooziewhatsit  Offline
master

Joined: Oct 2007
Posts: 3,884
Oregon
It really is pretty impressive what they're able to do now.

Quote
Enjoy unparalleled heating performance from one of our all-climate heat pump systems with Hyper-Heating INVERTER® (H2i®) technology. Hyper-heating systems can perform at 100 percent of rated capacity in outdoor ambient temperatures as low as 5° F with guaranteed operation down to -13° F. Available in select systems, H2i plus® technology increases the performance to 100 percent at temperatures as low as -5° F.


https://www.mitsubishicomfort.com/blog/mythbusters-heat-pumps-for-extreme-cold-climates

The cold side expansion gets, well, cold. Depending on the heat pump, it's around -40F. If the air temperature is -5F, that's still 35 degrees of heat that it can capture and move inside.


If you ever find yourself in a fair fight, your tactics suck.
Re: Any HVAC guys? Heat pump ?? [Re: hooziewhatsit] #3209212
01/30/24 01:47 PM
01/30/24 01:47 PM
Joined: Feb 2014
Posts: 1,706
central il.
S
second 70 Offline
top fuel
second 70  Offline
top fuel
S

Joined: Feb 2014
Posts: 1,706
central il.
Originally Posted by hooziewhatsit
It really is pretty impressive what they're able to do now.

Quote
Enjoy unparalleled heating performance from one of our all-climate heat pump systems with Hyper-Heating INVERTER® (H2i®) technology. Hyper-heating systems can perform at 100 percent of rated capacity in outdoor ambient temperatures as low as 5° F with guaranteed operation down to -13° F. Available in select systems, H2i plus® technology increases the performance to 100 percent at temperatures as low as -5° F.


https://www.mitsubishicomfort.com/blog/mythbusters-heat-pumps-for-extreme-cold-climates

The cold side expansion gets, well, cold. Depending on the heat pump, it's around -40F. If the air temperature is -5F, that's still 35 degrees of heat that it can capture and move inside.


I have a H2I and yeah it operates in the cold down to -15 but the problem is they can only run about 15 minutes below 0 before they go back to defrost for at least 10 minutes so they can't keep up. I checked it the other day @ 40 and it was producing heat at 115 well above the average of 55 over temp which would = 95.

Re: Any HVAC guys? Heat pump ?? [Re: second 70] #3209377
01/30/24 11:23 PM
01/30/24 11:23 PM
Joined: Jan 2003
Posts: 15,355
Omaha Ne
T
TJP Offline OP
I Live Here
TJP  Offline OP
I Live Here
T

Joined: Jan 2003
Posts: 15,355
Omaha Ne
Originally Posted by second 70
Wow that's quite a surprise. Gee without the backup electric you would have been 100% without heat.


I am sure they would have put a priority on it were that the case. I don't know that anyone would use a heat pump as their sole source of heat shruggy If so pretty gutsy IMO. I could have also used the oil filled radiant heaters that I already have for the shop and the fireplace. smile

Re: Any HVAC guys? Heat pump ?? [Re: 360view] #3209379
01/30/24 11:38 PM
01/30/24 11:38 PM
Joined: Jan 2003
Posts: 15,355
Omaha Ne
T
TJP Offline OP
I Live Here
TJP  Offline OP
I Live Here
T

Joined: Jan 2003
Posts: 15,355
Omaha Ne
Originally Posted by 360view
In your first post you mentioned noise and vibration, plus pushing down on a corner changing them.

That vibration should be a suspect in the root cause of the muffler crack.


Agreed, it may have been an indicator of things to come shruggy We only lifted very lightly on the one corner and the noise stopped. It came back about 2 hours later. Again a light "bumping" of the same corner stopped it altogether. The unit ran for at least 7-10 days before throwing the first code. But is was -25 when it did so which I'm told is not unusual. once things warmed up to -10 or so, I reset the unit it rans for about two hours and started wigging out.
The latest is the part is on order from carrier and hoped to be installed later this week or early next.
meanwhile our temps are in the 40's & 50's smile

Re: Any HVAC guys? Heat pump ?? [Re: second 70] #3209394
01/31/24 12:17 AM
01/31/24 12:17 AM
Joined: Oct 2007
Posts: 3,884
Oregon
hooziewhatsit Offline
master
hooziewhatsit  Offline
master

Joined: Oct 2007
Posts: 3,884
Oregon
Originally Posted by second 70
I have a H2I and yeah it operates in the cold down to -15 but the problem is they can only run about 15 minutes below 0 before they go back to defrost for at least 10 minutes so they can't keep up. I checked it the other day @ 40 and it was producing heat at 115 well above the average of 55 over temp which would = 95.


Yea, the defrost cycles don't help. It might have been the other thread I posted a video. In it, he says the three most important things when it comes to heat pumps (and other heat sources too) is:
1. Insulation.
2. Insulation.
3. Insulation.

laugh2

But really, if you live somewhere where it's routinely below 0F for long stretches, an air source heat pump probably isn't the best idea. But for 50 hours overnight over a couple weeks during a polar vortex? They're probably good enough.

I found an "Insulation 2.0" thing on youtube, about removing attic insulation, air sealing any gaps & cracks to the house below, then blowing insulation back in. I found and fixed a couple holes here, and am already noticing a difference.


If you ever find yourself in a fair fight, your tactics suck.