It would be fine. Only issue would be if you have a charcoal canister to scrub the fumes then another vent in the system would bypass it.
Got to call shenanigans on a tank collapsing under vacuum. At least a steel tank wouldn't. Motor would just be starved for fuel.
Usually it would starve for fuel but I have seen tanks get sucked in as well. IMO I don't think there could ever be enough vacuum to collapse a fuel tank if it is a
permeation compliant fuel tank as they are subjected to thousands of pressure/vacuum cycles as part of the compliance testing with extreme pressure and vacuum during that testing.
Here is the CARB procedure and it states
10,000 60-second cycles of pressure and vacuum.
Pressure Test
A pressure test shall be performed without fuel and prior to any other
portion of the durability demonstration or preconditioning of the fuel tank.
(a) Determine the fuel tank system’s design pressure and vacuum
limits under normal operating and storage conditions considering
the influence of any associated pressure/vacuum relief
components. To do this, measure the pressure limits using a fuel
tank from an evaporative emission control system that is not used
for any other portion of this test procedure by installing a
pressure transducer in the fuel tank. With the exception of the
use of the pressure transducer and connection to a carbon
canister, as applicable, the fuel tank and fuel tank configuration
used for these pressure measurements shall be identical to those
used in the remainder of this test procedure. Using compressed
air of no less than 21 °C, pressurize the fuel tank with compressed
air, seal the fuel tank, and measure the pressure every second for
5 minutes.
Use a vacuum pump to draw a vacuum in the fuel tank,
5 minutes. Record the maximum and minimum pressure
measurements on the test report. Subsection (b) of this test is not
required if the fuel tank pressure does not exceed a gauge
pressure of + 1.0 kPa for at least one minute when pressurized
and the fuel tank vacuum does not exceed a gauge pressure of
– 1.0 kPa for at least one minute when a vacuum is drawn in the
fuel tank.
(b) A pressure test shall be performed by sealing each fuel tank and
cycling the pressure between + 13.8 and − 3.4 kPa ( + 2.0 and
− 0.5 psig)
for 10,000 cycles at a rate of 60 seconds per cycle. If
normal operating or storage conditions cause pressure changes
greater than + 13.8 or – 3.4 kPa to accumulate in the fuel tanks,
cycle the pressure in the fuel tanks between the actual high and
low pressure limits experienced during normal operation or
storage. The tank pressure test shall be performed in a 49 ± 3 °C
environment with compressed air of no less than 21 °C.