Electrical Service disconnect question **update** #3127950
03/09/23 10:06 PM
03/09/23 10:06 PM
IMGTX Offline OP
IMGTX  Offline OP
My client sold a portion of their farm with a barn on it.
The sold barn has electricity that is run underground to a larger barn with the meter that is still my clients.
In a perfect world I would think disconnecting the power and pulling the underground wire would be the way to go but I do not know if it would be an option at this time.
If I do not pull the wire from the underground conduit, is there a specific codes compliant method to disconnecting the service and leaving the wire in place?
I would be concerned about just leaving the bare wires hanging loose outside of the box or inside the box even though there is no meter or service at the other end.
PS that is an old picture. Wasps have been removed and the conduits connected to the box correctly at this time.
Re: Electrical Service disconnect question [Re: IMGTX] #3127956
03/09/23 10:32 PM
03/09/23 10:32 PM
Kirkland, Washington
Pacnorthcuda Offline
Actually, the incoming power is the two hots at the top (your red line point to one of them). Is this the Box you want to kill or the feeder box??? You want to kill the hots (and ground) at the feeder box, which is likely as simple as Turing off the breakers at the feeder box.
Re: Electrical Service disconnect question [Re: IMGTX] #3127966
03/09/23 10:46 PM
03/09/23 10:46 PM
st.cloud fl
d-150 Offline
Smarter than a 5th grader?
d-150  Offline
st.cloud fl
Turn off the 200 amp bteaker
Re: Electrical Service disconnect question [Re: d-150] #3127973
03/09/23 11:18 PM
03/09/23 11:18 PM
IMGTX Offline OP
IMGTX  Offline OP
My apologies, I am terrible at descriptions but I know can turn off the breaker to disconnect the wires. What I really need to do is to disconnect those wires from the breaker box so the barn that was sold has no power. The new owner needs to get his own service and not use my clients.
If I leave off the 200 amp breaker I also shut off the barn and greenhouse, and they need to stay on.
I just want the disconnect to be safe so I referenced codes but it may just be unscrew and cover with tape.
I may be overthinking it and all I need to do is disconnect those wires and pull them out of the service box. But I worry that somebody would connect the other end to a new service by accident.
So when i disconnect these wires what do I do with them?
Re: Electrical Service disconnect question [Re: IMGTX] #3128034
03/10/23 09:19 AM
03/10/23 09:19 AM
Bitopia
jcc Offline
jcc  Offline
Bitopia
I am assuming the two wires fed from the lower bus bar lugs feed the remote barn. Obviously turn off and verify that you have de-energized the wires in question before you attempt anything.
You have three/four options IMO:
A, Disconnect the two wires and remove them from the conduit all the way back to the sold barn, with new owners' approval, sell wire for scrap/beer money.
B. Cut the wires, leave in the box and safely tape/insulate, which will make the wires forever too short and unusable.
C. Cut the conduit and tape the wires at ground level, plug the conduit hole to keep out wasps and backfill the hole of the cut conduit and forget. (leave the cut wires varying distances longer above the cut conduit, after taping/insulating cut ends, bend wire 180 degrees and shove ends back into the conduit before burying)
D. You can disconnect all the wires in the conduit, cut the conduit but not the wires at ground level, tape insulate the wires safely, and bury the coiled wires in the ground, allowing a future reconnect without too much hassle/cost. I prefer this option the least, but feel it should be mentioned.
Anyone qualified addressing the other end at the barn in the future would normally remove the wires from the other end, disable or remove them to their satisfaction. Anyone not qualified might ignore and/or do nothing, at their own potential peril.
I will not address the legality of doing any of the above regarding local codes, but everything I have noted above I believe to be safe practice. It would be proper to tag the wires at the other ends as disconnected feeders with a date.
Re: Electrical Service disconnect question [Re: jcc] #3128062
03/10/23 10:36 AM
03/10/23 10:36 AM
North Dakota
6PakBee Offline
6PakBee  Offline
North Dakota
Cut them short in the box and use these in the correct size.
Heat Shrink Cable Caps
Re: Electrical Service disconnect question [Re: jcc] #3128065
03/10/23 10:37 AM
03/10/23 10:37 AM
IMGTX Offline OP
IMGTX  Offline OP
I am hoping for Option A
I may have to settle for Option B
The pull is about 600 feet and I can not see me pulling the wire out without a lot of help that I don't have. Tempted to hook it up to the tucks bumper and hope for the best. LOL
Even though every electrician I have seen out here is licensed, a lot of this farms electrical is not up to code. That is why I am concerned about leaving them in place.
Chances are the same nutcase who installed all this will end up at the barn that was sold and I don't want him to do anything that would effect my client.
Re: Electrical Service disconnect question [Re: IMGTX] #3128077
03/10/23 11:21 AM
03/10/23 11:21 AM
N.W. Florida
Fat_Mike Offline
Fat_Mike  Offline
N.W. Florida
Disclaimer: I'm not an electrician
If you leave wires from the barn to the house (or wherever that box is), whenever the new owners restores power, those (now) loose wires will become energized; a potentially deadly hazard.
I'd (permanently) cut the power from both ends. Whether you pull the wire is up to you.
Re: Electrical Service disconnect question [Re: Fat_Mike] #3128097
03/10/23 12:01 PM
03/10/23 12:01 PM
Calgary, Alberta Canada
a12rag Offline
a12rag  Offline
Turn off the main breaker, remove the feeder wires at the bottom, along with the lugs. Don't forget to remove the "neutral wire" that is going to the neutral block on right side of main bus in picture. Cut the wires at the conduit. Reinstall the cover, then turn main breaker back on. Next I would cut the conduit and wires inside, maybe a couple inches above ground (??) and then put a plug on the end. As well, put a hole cover on bottom of panel where conduit used to go into panel. I would say it's up to you if you want to leave the wire or pull it out of the conduit . . .
Re: Electrical Service disconnect question [Re: a12rag] #3128117
03/10/23 12:42 PM
03/10/23 12:42 PM
Midwest
MoparsnMissiles Offline
Midwest
As stated previously, you need to make the disconnect at BOTH ends. You don't want someone in the future to be energizing those lines again from the other end, even if they are disconnected on your end.
I am also questioning if in fact the cable is actually in "Conduit" the entire 600' to the other barn? Often, (more often than not) this cable is direct burial and the conduit you see above ground on both ends only goes a couple feet down below surface and then ends. If this is the case, you will play H**L trying to "pull" this cable. Gonna need a BIGGER truck to pull that one!
Re: Electrical Service disconnect question [Re: MoparsnMissiles] #3128137
03/10/23 01:18 PM
03/10/23 01:18 PM
Byron, NY
W.I.N. Racing Offline
Byron, NY
iagree
'01 P1500, Blown/Inj BAE,/Veney ,Bruno/CS2,Dana 60
'01 Dodge 3500 S Cummins Auto, Fresh air kit, 4" Exhaust,
'05 Dodge Magnum R/T - Too Much to list
'60 Willys CJ5
'01 International LPX - Project,DT466, Allison
'64 Plymouth Valiant, Inj 528 Hemi, 2spd
Re: Electrical Service disconnect question [Re: W.I.N. Racing] #3128154
03/10/23 02:10 PM
03/10/23 02:10 PM
New Jersey
P
Powerflow Offline
Powerflow  Offline
P
New Jersey
I'd hire a licensed electrician and have them de-energize the feed to the barn. They'd be knowledgeable about the right way to
terminate the wires. You don't want to do something unsafe and be responsible if there's a problem.
Re: Electrical Service disconnect question **update** [Re: IMGTX] #3128254
03/10/23 08:34 PM
03/10/23 08:34 PM
IMGTX Offline OP
IMGTX  Offline OP
Thank you all for the advice.
Just got back and found they sold 2 barns with lots.
I got the approval to remove the wire between the barns.
I had not thought about the wire being direct burial. Very good point, as was cutting offset lengths and everything else too.
One set (pictured above) could be direct burial and one definitely is not direct burial grade wire, but hey they screwed up so much it's a fifty fifty chance.
Today I disconnected both ends of the power and sealed the ends.
Next weekend I am going to start pulling the cable out of the conduit. If it is direct buried then I will cut it even with the ground at both ends and call it a day.
Any good ideas on how to pull it?
I like the idea of recycling it for beer money. It will probably be gas money but just as good. up
I was thinking an engine crane to get it started gently and then literally hooking it to the truck and pulling away. Nothing needs to be saved as long as I do not damage the barns.
Re: Electrical Service disconnect question **update** [Re: IMGTX] #3128332
03/11/23 09:15 AM
03/11/23 09:15 AM
North Dakota
6PakBee Offline
6PakBee  Offline
North Dakota
If you have settled on trying to pull the wire out, don't cut if off even with the ground, you need something to attach to. And most important, wait until the spring thaw is about over, the ground is softest and if the wire can be pulled, this is when it can be. As to what to use, a winch is probably the best. If you don't have a winch, a font end loader is probably a good choice. One of my friends has a fairly large CAT and last spring we were pulling out tree stumps up to about a foot with it and a long chain.
Re: Electrical Service disconnect question **update** [Re: IMGTX] #3128365
03/11/23 11:13 AM
03/11/23 11:13 AM
N.W. Florida
Fat_Mike Offline
Fat_Mike  Offline
N.W. Florida
That or a tractor, if one is available. Since you're recycling it, bring some bolt cutters along in case you need to lop it off for any reason.
Re: Electrical Service disconnect question **update** [Re: IMGTX] #3128379
03/11/23 11:39 AM
03/11/23 11:39 AM
Unfortunately back in New York
N
Nukechargerboy Offline
N
You'll get more beer moneyu if it's clean. Strip the insulation off and now you get more $$$
Re: Electrical Service disconnect question **update** [Re: IMGTX] #3128417
03/11/23 01:15 PM
03/11/23 01:15 PM
central il.
second 70 Offline
second 70  Offline
central il.
As a lineman for over 40 years I'm guessing from your picture that it's direct buried #2 alum triplex and is only in conduit from the ground to the box's on each end.
Re: Electrical Service disconnect question **update** [Re: second 70] #3128476
03/11/23 04:06 PM
03/11/23 04:06 PM
moparx Offline
moparx  Offline
disconnect from both ends as has already been stated.
you do NOT want to see LIGHTNING BOLTS in front of your eyeballs.................[i'm speaking from experience ! panic laugh2
my one cousin who is a licensed electrician, laffed his AZZ off when i asked him to help, and told him what happened. haha
beer
Re: Electrical Service disconnect question **update** [Re: IMGTX] #3128642
03/11/23 11:35 PM
03/11/23 11:35 PM
Candler,NC / Myrtle Beach, SC
JDMopar Online content
JDMopar  Online Content
If that wire is direct buried, there's no way in the world you'll pull it out. If it's in pipe, it may pull, but it won't be easy. That is 2/0 direct bury UG triplex and it is wrapped together from one end to the other. You will have to pull all 3 wires at the same time. If you can get a Kellum grip (works like Chinese handcuffs) to slide down over the wires when you get them out of the box, that will make them easier to pull. If you have a BIG tractor handy that has a front bucket loader, you could catch the wire as low as you can, then raise the bucket up to pull it out of the pipe. Repeat that about 872 times and you'll have it out! LOL. Good luck to you. It will be a lot of work for no more money than you will get out of it.
You can buy a cover at the electrical supply house for a few bucks to close up that hole the conduit and wire went thru. Close up the hole the bare ground goes out of with plumbers putty or caulk to keep the wasps and dirt dobbers out.
Re: Electrical Service disconnect question [Re: jcc] #3128665
03/12/23 01:19 AM
03/12/23 01:19 AM
it is time for you to call a good electrician and have them do that work properly so it is up to your local code twocents
