Re: Electrical Meter/Service question
[Re: IMGTX]
#3088263
10/22/22 10:31 AM
10/22/22 10:31 AM
Posts: 10,714 North Dakota
6PakBee
North Dakota
PVC conduit from the green house box to ground, trench, PVC conduit from ground up pole with weather head at top of conduit. USE cable.
[Re: srt]
#3088505
10/23/22 09:43 AM
10/23/22 09:43 AM
6PakBee
North Dakota
Conduit in trench is important within the greenhouse no pvc or flex plastic. Make sure to not undersize the circuits (add up anticipated loads) and install a disconnect at the greenhouse before the branch circuits.. Make sure all the runs are thwn in conduit and carry a ground. Needs to be designed for "wet locations" and gcfi's.. Insure electrician properly grounds and does not energize the frame of the greenhouse. Additionally any cable used to lighting or equipment should be rated sjoow. I thought the OP said the greenhouse was "pre-wired" and only needed the service entrance?
[Re: 6PakBee]
#3088786
10/24/22 10:40 AM
10/24/22 10:40 AM
Posts: 12,234 Looking for a way out of Middl...
IMGTX
Thank you all for the information. It is exactly what I needed to know. I am looking at getting a pole installed and will call an electrician for the hookup. I will dig the trench over to the greenhouse for the conduit. The idea the current electrician has of trenching to the barn is going to hit a snag because there is a water main crossing between the two. I know for a fact that the main is not as deep as it should be and it will be a problem I don't' want to address. Thanks again
[Re: 6PakBee]
#3088809
10/24/22 12:19 PM
10/24/22 12:19 PM
Posts: 15,754 Jefferson State
srt
ESYC
ESYC
Jefferson State
Conduit in trench is important within the greenhouse no pvc or flex plastic. Make sure to not undersize the circuits (add up anticipated loads) and install a disconnect at the greenhouse before the branch circuits.. Make sure all the runs are thwn in conduit and carry a ground. Needs to be designed for "wet locations" and gcfi's.. Insure electrician properly grounds and does not energize the frame of the greenhouse. Additionally any cable used to lighting or equipment should be rated sjoow. I thought the OP said the greenhouse was "pre-wired" and only needed the service entrance? Prewired only indicates it's there. No indication of code or suitability. The "cable" pertains to that used from gcfi to fixture or appliance. Greenhouses degrade due to exposure, UV and moisture. Locally there are lots of greenhouses, some done right, some are shocking experiences.
[Re: srt]
#3088847
10/24/22 02:09 PM
10/24/22 02:09 PM
Posts: 19,402 north of coder
moparx
"some are shocking experiences".................. one of my first jobs in life was in the 7th grade. a few of us kids would ride ride the school bus that went to the outskirts of town where a greenhouse was located, that was owned by the parents of another kid we knew in school. i'll never forget the pay scale quote : "5 cents for the little boxes and 10 cents for the big boxes. the more ya do, the more ya make. and if you do good during the week, you can work saterday with Ears...." [that was a grownup doofus that tended the coal furnace and did repairs to the greenhouse structure] some, or should i say MOST of the wiring in that place, was done using the "best" cheapo extension cords and multi-plug adapters the local 5&10 store had to offer.
[Re: srt]
#3089288
10/26/22 09:17 AM
10/26/22 09:17 AM
6PakBee
North Dakota
Conduit in trench is important within the greenhouse no pvc or flex plastic. Make sure to not undersize the circuits (add up anticipated loads) and install a disconnect at the greenhouse before the branch circuits.. Make sure all the runs are thwn in conduit and carry a ground. Needs to be designed for "wet locations" and gcfi's.. Insure electrician properly grounds and does not energize the frame of the greenhouse. Additionally any cable used to lighting or equipment should be rated sjoow. I thought the OP said the greenhouse was "pre-wired" and only needed the service entrance? Prewired only indicates it's there. No indication of code or suitability. The "cable" pertains to that used from gcfi to fixture or appliance. Greenhouses degrade due to exposure, UV and moisture. Locally there are lots of greenhouses, some done right, some are shocking experiences. A product for sale to the general public with pre-wired electrical that doesn't meet the NEC? Hmm.
Re: Electrical Meter/Service question *update*
[Re: IMGTX]
#3089826
10/28/22 09:15 AM
10/28/22 09:15 AM
6PakBee
North Dakota
Currently the box on the greenhouse has a single bus bar for power to all 4 breakers and one connection for ground/return.
I will have to replace the box with one that has 2 power buses and one ground/return.
I may be using the wrong terminology but hopefully that makes sense. Do you have a picture of the internals of the greenhouse service entrance? Having four, 20 ampere breakers on a single 110 volt feeder seems odd.
[Re: IMGTX]
#3089880
10/28/22 12:27 PM
10/28/22 12:27 PM
Posts: 1,707 central il.
second 70
central il.
You are correct, I was wrong.
After looking at the box diagram from the manufacturer I realized that there are 2 buss bars. One connects at the top and one in the middle.
I only saw the middle buss connector when I first looked but it does have 2.
My concern is if I can split the 240v 50amp dual pole breaker into two 120v 50amp circuits?
All you need to do is run 1 leg off the 50amp breaker to each terminal lug on green house box. ( one wire from each screw on 50 amp breaker to green house main lug connection) No need to chance it to 2 single 50's. Double breakers will both trip even if only 1 side is overloaded. You must run wire rated for 50 amps between boxes. The 50amp breaker is to protect the feed circuit. I bet that's at least a 60 amp rated box on green house. As it's wired you need 40amp per leg. The 20 amp breakers protect the load. And be careful the service coming out the bottom isn't really fused. The 200 amp main is it's only protection and that looks like 2agw which is only good for 100 amps. Needs reattached and a bushing installed too.
[Re: IMGTX]
#3090056
10/28/22 09:25 PM
10/28/22 09:25 PM
6PakBee
North Dakota
There is a basic question that only the electrical inspector (Authority Having Jurisdiction) can answer.
Is the green house a feeder circuit or a service entrance?
The answer will determine what kind of underground wire is permissible and how many conductors you will need. As to your feeder breaker sizing, that is dependent on the wire size or vice versa, the feeder breaker size is dependent on the wire size. As has been mentioned, determine what the current rating of the greenhouse entrance box and size the wiring and breaker accordingly. It is a common misconception that a distribution panel has to be fed at the panel rating. You can feed a 60 ampere panel with 20 amp breakers but obviously that would be a questionable thing to do.