Question for electricians here. My little house has 300 amp service actually 2 x 150amp that goes to 2 150A panels .
Which panel is the neutral-ground point? Since you can only have one NG point. I have been researching generators and got me wondering.I know could just take the panel covers off and look but I wouldn't know why one vs the other,
Thanks for any info.

Re: Electricians;Neutral-Gnd Bonding [Re: RTSE4ME] #3134989
04/04/23 09:31 AM
04/04/23 09:31 AM
Joined: Oct 2005
Posts: 8,867
Ontario, Canada
S
Stanton Offline
Don't question me!
Stanton  Offline
Don't question me!
S

Joined: Oct 2005
Posts: 8,867
Ontario, Canada
Are these fed
a) each from a separate meter or
b) each fed separately from a single meter
c) one panel is fed from the other

Re: Electricians;Neutral-Gnd Bonding [Re: RTSE4ME] #3134992
04/04/23 09:35 AM
04/04/23 09:35 AM
Joined: Jan 2003
Posts: 10,707
North Dakota
6PakBee Offline
I Live Here
6PakBee  Offline
I Live Here

Joined: Jan 2003
Posts: 10,707
North Dakota
Originally Posted by RTSE4ME
Question for electricians here. My little house has 300 amp service actually 2 x 150amp that goes to 2 150A panels .
Which panel is the neutral-ground point? Since you can only have one NG point. I have been researching generators and got me wondering.I know could just take the panel covers off and look but I wouldn't know why one vs the other,
Thanks for any info.


Both are. From the 2017 NEC:

250.58 Common Grounding Electrode. Where an ac system is
connected to a grounding electrode in or at a building or struc‐
ture, the same electrode shall be used to ground conductor
enclosures and equipment in or on that building or structure.
Where separate services, feeders, or branch circuits supply a
building and are required to be connected to a grounding elec‐
trode(s), the same grounding electrode(s) shall be used.


"We live in a time when intelligent people are being silenced so that stupid people won't be offended".
Re: Electricians;Neutral-Gnd Bonding [Re: Stanton] #3134999
04/04/23 10:01 AM
04/04/23 10:01 AM
Joined: Jan 2003
Posts: 2,042
MD
RTSE4ME Offline OP
top fuel
RTSE4ME  Offline OP
top fuel

Joined: Jan 2003
Posts: 2,042
MD
Originally Posted by Stanton
Are these fed
a) each from a separate meter or
b) each fed separately from a single meter
c) one panel is fed from the other


b) each fed separately from a single meter

One panel contains mostly 120v loads, Second panel has well pump, heat pump and furnace (90A breaker that goes to small sub panel).

Re: Electricians;Neutral-Gnd Bonding [Re: RTSE4ME] #3135013
04/04/23 10:40 AM
04/04/23 10:40 AM
Joined: Nov 2003
Posts: 12,494
Western Colorado High Desert
moparmarks Offline
I Live Here
moparmarks  Offline
I Live Here

Joined: Nov 2003
Posts: 12,494
Western Colorado High Desert
So all the panels are on the same structure?
The bond need to be at the first or main point of disconnect. So if you have one meter feeding a main panel the bond needs to be at that panel. If you have a meter feeding a main braker or disconnect then to a panel then the bond needs to be in the disconnect switch.


72 Satellite Sebring Plus 440, 72 Dart 5.9 4-spd, 68 Valiant, 73 W200, 78 D100 sb, 78 D200, 98 DAKOTA, .
Moparmarks Parts & Restorations
Desert Mopar Metal
Grand Jct. CO
970-261-7039
http://moparmark.com/
motormangj@gmail.com
Re: Electricians;Neutral-Gnd Bonding [Re: 6PakBee] #3135015
04/04/23 10:47 AM
04/04/23 10:47 AM
Joined: Jan 2003
Posts: 2,042
MD
RTSE4ME Offline OP
top fuel
RTSE4ME  Offline OP
top fuel

Joined: Jan 2003
Posts: 2,042
MD
Originally Posted by 6PakBee
Originally Posted by RTSE4ME
Question for electricians here. My little house has 300 amp service actually 2 x 150amp that goes to 2 150A panels .
Which panel is the neutral-ground point? Since you can only have one NG point. I have been researching generators and got me wondering.I know could just take the panel covers off and look but I wouldn't know why one vs the other,
Thanks for any info.


Both are. From the 2017 NEC:

250.58 Common Grounding Electrode. Where an ac system is
connected to a grounding electrode in or at a building or struc‐
ture, the same electrode shall be used to ground conductor
enclosures and equipment in or on that building or structure.
Where separate services, feeders, or branch circuits supply a
building and are required to be connected to a grounding elec‐
trode(s), the same grounding electrode(s) shall be used.


Does this mean that two services are connected together only through one electrode?

Re: Electricians;Neutral-Gnd Bonding [Re: moparmarks] #3135016
04/04/23 10:50 AM
04/04/23 10:50 AM
Joined: Jan 2003
Posts: 2,042
MD
RTSE4ME Offline OP
top fuel
RTSE4ME  Offline OP
top fuel

Joined: Jan 2003
Posts: 2,042
MD
Originally Posted by moparmarks
So all the panels are on the same structure?
The bond need to be at the first or main point of disconnect. So if you have one meter feeding a main panel the bond needs to be at that panel. If you have a meter feeding a main braker or disconnect then to a panel then the bond needs to be in the disconnect switch.

yes, both panels mounted 1/2" apart.

Re: Electricians;Neutral-Gnd Bonding [Re: RTSE4ME] #3135019
04/04/23 10:55 AM
04/04/23 10:55 AM
Joined: Jan 2010
Posts: 1,087
st.cloud fl
D
d-150 Offline
Smarter than a 5th grader?
d-150  Offline
Smarter than a 5th grader?
D

Joined: Jan 2010
Posts: 1,087
st.cloud fl
Actual grounding electrode wire should start at 1 panel go to 2 panel then to grounding electrode

Re: Electricians;Neutral-Gnd Bonding [Re: d-150] #3135020
04/04/23 10:57 AM
04/04/23 10:57 AM
Joined: Jan 2010
Posts: 1,087
st.cloud fl
D
d-150 Offline
Smarter than a 5th grader?
d-150  Offline
Smarter than a 5th grader?
D

Joined: Jan 2010
Posts: 1,087
st.cloud fl
And if the panels conduit between panels is metal they should have bonding bushings

Re: Electricians;Neutral-Gnd Bonding [Re: moparmarks] #3135023
04/04/23 11:07 AM
04/04/23 11:07 AM
Joined: Jan 2003
Posts: 4,270
Morrow, OH
markz528 Offline
master
markz528  Offline
master

Joined: Jan 2003
Posts: 4,270
Morrow, OH
Originally Posted by moparmarks
So all the panels are on the same structure?
The bond need to be at the first or main point of disconnect. So if you have one meter feeding a main panel the bond needs to be at that panel. If you have a meter feeding a main braker or disconnect then to a panel then the bond needs to be in the disconnect switch.


This is correct.

Do you have 2 meters or 1? In general, I don't believe that code allows multiple services to feed a single residence but I would need to look it up to be sure. Really need more info to properly answer your question.


67 Coronet 500 9.610 @ 139.20 mph
67 Coronet 500 (street car) 14.82 @ 94 mph
69 GTX (clone) - build in progress......
Re: Electricians;Neutral-Gnd Bonding [Re: markz528] #3135050
04/04/23 12:20 PM
04/04/23 12:20 PM
Joined: Feb 2014
Posts: 1,701
central il.
S
second 70 Offline
top fuel
second 70  Offline
top fuel
S

Joined: Feb 2014
Posts: 1,701
central il.
The neutral is the wire that is part of the 3 wire service and hooks up to the large buss in panel. Normally bare on overhead service, yellow coated on underground direct bury cable, but can be a regular black wire with white tape. The ground is a wire that is smaller normally bare and go's to ground rod at base and hooks to the other bare buss in the panel.

Re: Electricians;Neutral-Gnd Bonding [Re: second 70] #3135066
04/04/23 01:00 PM
04/04/23 01:00 PM
Joined: Nov 2003
Posts: 12,494
Western Colorado High Desert
moparmarks Offline
I Live Here
moparmarks  Offline
I Live Here

Joined: Nov 2003
Posts: 12,494
Western Colorado High Desert
Originally Posted by second 70
The neutral is the wire that is part of the 3 wire service and hooks up to the large buss in panel. Normally bare on overhead service, yellow coated on underground direct bury cable, but can be a regular black wire with white tape. The ground is a wire that is smaller normally bare and go's to ground rod at base and hooks to the other bare buss in the panel.


Yes and they both need to be bonded together at the first point of disconnect on a structure.


72 Satellite Sebring Plus 440, 72 Dart 5.9 4-spd, 68 Valiant, 73 W200, 78 D100 sb, 78 D200, 98 DAKOTA, .
Moparmarks Parts & Restorations
Desert Mopar Metal
Grand Jct. CO
970-261-7039
http://moparmark.com/
motormangj@gmail.com
Re: Electricians;Neutral-Gnd Bonding [Re: RTSE4ME] #3135111
04/04/23 02:44 PM
04/04/23 02:44 PM
Joined: Jan 2003
Posts: 10,707
North Dakota
6PakBee Offline
I Live Here
6PakBee  Offline
I Live Here

Joined: Jan 2003
Posts: 10,707
North Dakota
Originally Posted by RTSE4ME
Originally Posted by 6PakBee
Originally Posted by RTSE4ME
Question for electricians here. My little house has 300 amp service actually 2 x 150amp that goes to 2 150A panels .
Which panel is the neutral-ground point? Since you can only have one NG point. I have been researching generators and got me wondering.I know could just take the panel covers off and look but I wouldn't know why one vs the other,
Thanks for any info.


Both are. From the 2017 NEC:

250.58 Common Grounding Electrode. Where an ac system is
connected to a grounding electrode in or at a building or struc‐
ture, the same electrode shall be used to ground conductor
enclosures and equipment in or on that building or structure.
Where separate services, feeders, or branch circuits supply a
building and are required to be connected to a grounding elec‐
trode(s), the same grounding electrode(s) shall be used.


Does this mean that two services are connected together only through one electrode?


Yes.


"We live in a time when intelligent people are being silenced so that stupid people won't be offended".
Re: Electricians;Neutral-Gnd Bonding [Re: 6PakBee] #3135165
04/04/23 03:18 PM
04/04/23 03:18 PM
Joined: Jan 2003
Posts: 2,042
MD
RTSE4ME Offline OP
top fuel
RTSE4ME  Offline OP
top fuel

Joined: Jan 2003
Posts: 2,042
MD
Thank You .....makes sense.
Nice to have a better understanding when Electrician comes out for estimate.

Re: Electricians;Neutral-Gnd Bonding [Re: RTSE4ME] #3135364
04/04/23 06:39 PM
04/04/23 06:39 PM
Joined: Nov 2003
Posts: 12,494
Western Colorado High Desert
moparmarks Offline
I Live Here
moparmarks  Offline
I Live Here

Joined: Nov 2003
Posts: 12,494
Western Colorado High Desert
Okay you asked about a neutral-ground point not about the ground rod which are not the same.


72 Satellite Sebring Plus 440, 72 Dart 5.9 4-spd, 68 Valiant, 73 W200, 78 D100 sb, 78 D200, 98 DAKOTA, .
Moparmarks Parts & Restorations
Desert Mopar Metal
Grand Jct. CO
970-261-7039
http://moparmark.com/
motormangj@gmail.com
Re: Electricians;Neutral-Gnd Bonding [Re: moparmarks] #3135375
04/04/23 07:11 PM
04/04/23 07:11 PM
Joined: Jan 2003
Posts: 2,042
MD
RTSE4ME Offline OP
top fuel
RTSE4ME  Offline OP
top fuel

Joined: Jan 2003
Posts: 2,042
MD
He answered that . Both are.
Or am I missing something

Re: Electricians;Neutral-Gnd Bonding [Re: RTSE4ME] #3135479
04/05/23 01:44 AM
04/05/23 01:44 AM
Joined: Nov 2003
Posts: 12,494
Western Colorado High Desert
moparmarks Offline
I Live Here
moparmarks  Offline
I Live Here

Joined: Nov 2003
Posts: 12,494
Western Colorado High Desert
No I guess I'm missing something.


72 Satellite Sebring Plus 440, 72 Dart 5.9 4-spd, 68 Valiant, 73 W200, 78 D100 sb, 78 D200, 98 DAKOTA, .
Moparmarks Parts & Restorations
Desert Mopar Metal
Grand Jct. CO
970-261-7039
http://moparmark.com/
motormangj@gmail.com






Powered by UBB.threads™ PHP Forum Software 7.7.1